Issue
An issue has been identified when a Unifact configuration is downloaded to a Unifact controller where the first byte of the download is incorrectly set to 0.
Environment
VisiSat 2.1
Cause
When downloading a Unifact configuration to a Unifact controller the first byte is set to 0.
The node links should be
Resolution
Download the required scheme to the Unifact controller.
It does not matter if this is a new scheme for the controller or you are re-downloading the same scheme the controller already contains.
Enter Bubbleland
A links mis-match message is displayed.
Select the Fix Later option.
Concentrating on any object link,
Break the link
Then re-make the link
This re-writes the configuration's node link tables in the controller and the configuration now has matching node links.
Conformation that the configuration is now correct is provided when you enter Bubbleland the next time.
The controller configuration now matches the configuration in VisiSat.
Note:
This procedure will need to be carried out each time the controller's configuration is downloaded.