Large key/card numbers directly to individuals

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Large key/card numbers directly to individuals
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1540 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Large key/card numbers directly to individuals

Picard Product_Support
‎2018-09-06 11:41 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:50 AM

Issue

Are there any advantages for assigning large key/card numbers directly to individuals rather than using key/card translations tables?

Environment

I/NET Site

define card translation, card number=individual number

Cause

Client is using same facility code but card numbers are not continuous ranging from 1000 to 4000 and 54000 above. In case the quantity of cards go beyond 32000 is it possible to add these cards to I/NET since each tenant can only take 32000 cards? Having cards with numbers both below 32000 and above, do I have to define card translations for both?.

Resolution

Large Card support allows you to:

  • Order cards with numbers greater than 32000
  • Enable individuals to have multiple simultaneous cards during card replacement projects
  • Allows you to replace an individuals card without creating a new individual in the I/NET system

INET does support up to 6 million cards but here is the catch. It is 32,000 individuals per tenant, and up to 64,000 individuals per door if you have an SCU or 7920 (with that 48K memory board attached).

What this means is each tenant group can be up to 32,000 individuals. You can put cards in, as long as their in the same facility code to make the 32,000 individuals limit. If you define card translation, then you are able to go over the 32000 as far as the card number. 32,000 is the individual number with a standard 26-bit Wiegand card with the max card number is 65,535. So if you do large number the 32,000 individual number could be a card that actually has 65535 as the card number. For Example you have cards 1 through 32,000 but missing 10,001 through 10,999, then you will have to have to define card translation so you can have card numbers greater than 32,000.

32,000 is the total for individuals. But if you are using Card number equals individuals, it will not accept anything over 32000. it will only work if you are using big card numbers.

 

Go to TCON 300, page 9-5 (INET Seven Technical Reference Guide) for more information.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1232
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore