LON SNVT on a shadow object in a Niagara R2 UNC station takes 2-3 minutes to update after an override command
  • LON SNVT on a shadow object in a Niagara R2 UNC station takes 2-3 minutes to update after an override command
  • sesa116871
    sesa116871
‎2018-09-06 02:57 PM
A LON SNVT on a shadow object in a Niagara R2 UNC station takes 2-3 minutes to update after an override command is issued from a graphic.
  • Niagara R2 UNC
Minimum and maximum send times are not set correctly.
  1. Verify the maxSendtime and minSendtime parameters in the Local Lon Device > Config tab have the appropriate values (default values are 100 and 5 seconds respectively).   The minSendtime parameter specifies the minimum amount of time that the controller will wait before updating values.
  2. Re-upload the affected LON object from the LON controller.
  3. Re-bind the Lon object in the Lon Link Manager.
  • TAC IA Series
  • 2655