LNS database runs extreme slowly in TAC Vista Workstation on a separate PC

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LNS database runs extreme slowly in TAC Vista Workstation on a separate PC
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa64461
    sesa64461

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1929 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LNS database runs extreme slowly in TAC Vista Workstation on a separate PC

Picard Product_Support
‎2018-09-10 07:54 AM

Issue

User can open the database in TAC Vista Workstation, but can not run the project database with an LNS network properly when it has been copied from the project site.

TAC Vista Workstation is extremely slow when the user operates it in a separate PC or laptop.

Product Line

TAC Vista

Environment

  • Vista 5.1.X
  • Windows Environment
  • LonMaker / NL220
  • Vista System Plug-In

Cause

In the user's PC or laptop, the Vista database can not find the proper LNS port which exists in the project site PC.

Resolution

  1. Define the database which was copied from the project site as the active database in the "Vista Database" tab in "TAC Vista Server Setup"
  2. Run TAC Vista Server application (TACOS.exe)
  3. Run TAC Vista Workstation. Wait a while for the TAC Vista Workstation to open the database completely
  4. Right click the LNS port. Wait a while for the right-click options to appear, then click "Properties"
  5. Record the port name in TAC Vista Workstation and its "Device address" in the properties window to a TXT file and save it.
  6. Delete all text in the "Device address" in the properties window, and click "OK" to accept the change
  7. Repeat steps 4, 5, and 6 to delete all LNS ports' "Device address"

After the last "Device address" has been deleted. The TAC Vista Workstation's response speed will be back to normal.

If some modifications have been made to the database and need to be applied in the project (which means the database would replace the project site database), remember to restore the "Device address" name according to the TXT file before restoring on the site PC.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 8036
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore