JavaScript function to determine if a TGML graphic is being run in Workstation or Webstation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • JavaScript function to determine if a TGML graphic is being run in Workstation or Webstation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2203 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

JavaScript function to determine if a TGML graphic is being run in Workstation or Webstation

Picard Product_Support
‎2018-09-06 01:27 PM

Issue

Is it possible to determine if a TGML graphic is being run in Workstation or Webstation?

Environment

TGML Graphics Editor 1.1.X

Vista 5.1.X Workstation

TacWebApps 5.1.X (Webstation)

Cause

There are differences in the rendering of graphics between Workstation and Webstation. Sometimes this leads to the necessity of creating two sets of components depending on where the graphics will be presented. By being able to programmatically determine the environment, one set of components can be used regardless of the presentation, reducing engineering time.

Resolution

The results of the JavaScript function Packages.java.lang.System.getProperty can determine whether the viewer is currently in Vista Workstation or not. 
 
Note: This is not a supported function in TGML. Because it is unsupported, it is subject to change without notification, and should be used accordingly at your own risk.
 
  1. Create a document-level script tag that runs OnDocumentLoad.
  2. Determine the current Vista version (and keep potential future upgrades in mind as well). The implementation of the property changed in an upgrade from Vista 5.1.4 to Vista 5.1.5.
    • If the system is Vista version 5.1.4 and prior, use the following function:

      if (Packages.java.lang.System.getProperty("browser") == "ActiveX Scripting Host")

      If the statement is true, then the graphic is being run in Workstation.
    • If the system is Vista version 5.1.5 and later, use the following function

      if (Packages.java.lang.System.getProperty("java.runtime.name") == "IKVM.NET")

      If the statement is true, then the graphic is being run in Workstation.

    • The following script can be run for any version of Vista 5.

      /*
        returns what browser Tgml is viewed in (Workstation==false,Webstation/Webserver==true)
       */
      var getBrowserType = function() {  
       var browser = false; // initiates browser indication variable as Webstation/Webserver
       if (Packages.java.lang.System.getProperty("browser") != null) { // checks Vista version
        // evaluated for Vista is 5.1.4 or earlier
        if (Packages.java.lang.System.getProperty("browser") == "ActiveX Scripting Host") {
            browser = false;   // indicates variable as Workstation
        } else {
           browser = true;    // indicates variable as Webstation/Webserver
          }
       } else {
        // evaluated for Vista 5.1.5 or later
        if (Packages.java.lang.System.getProperty("java.runtime.name") == "IKVM.NET") {
         browser = false;   // indicates variable as Workstation
        } else {
         browser = true;    // indicates variable as Webstation/Webserver
        }
       }
        return browser;     // returns browser indication
      } 
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5865
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore