Jace 8000 Serial Debug System Shell

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Jace 8000 Serial Debug System Shell
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8008 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Jace 8000 Serial Debug System Shell

Guinan RandyDavis Guinan
‎2020-04-02 12:08 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:35 AM

Issue

How to connect to the Jace 8000 system shell

Product Line

TAC IA Series

Environment

I/A Series Jace 8000

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Multiple diagnostic and low-level configuration processes need to be performed directly connected to the Jace 8000 in the system shell of the device.

Resolution

  1. Connect the USB cable between the controller’s Debug port and the USB port you are using on your PC
     Debug_1.jpg
  2. On your PC, start your terminal emulation software. For example to start PuTTY from the Windows
    Start menu, this is typically Programs > PuTTY → PuTTY. PuTTy can be downloaded at no cost if you do not already have it on your PC.
  3. In the tree in the PuTTY Configuration dialog, expand Connection and click Serial.Debug_2.jpg
  4. Set the “Serial line to connect to” for your PC’s (USB) COM port to use. For example, COM3.
    NOTE: You can examine Ports in Windows Device Manager to determine which serial port is in use on the PC. If you don't see the Jace in the COM ports, you will need to install the driver which can be Downloaded from FTDI.  It is also attached to this document below for Win10.
  5. Set the “Configure the serial line” fields as follows:
    • Speed (baud): 115200
    • Data bits: 8
    • Stop bits: 1
    • Parity: None
    • Flow control: None
  6. In the tree in the PuTTY Configuration dialog, click Session and then click/select the “Connection
    type” as Serial
    NOTE: (Optional) You can save this configuration to reuse (load) in future PuTTY to JACE serial sessions.
    To do this, type in a connection name in the “Saved Sessions” field (for example, “JACE-
    8000-S”), and click Save.
    When you start PuTTY again to serially connect to the JACE, select this name and click Load.
  7. At the bottom of the PuTTY Configuration dialog, click Enter.
  8. At the login prompt, enter a platform user name, and at the password prompt, the platform
    password.
    a. If prompted for system passphrase, enter the platform’s system passphrase.
    If login is successful, the TITAN System Shell menu appears.
  9. When finished making platform changes from the system shell, do the following:
    • If no changes or reboot is not necessary, simply type L to Logout.
    • If changes require rebooting, select the Reboot option.
    Type “y” at the “Are you sure you want to reboot [y/n]” prompt, and press Enter.
    Shutdown-related text appears in the terminal (PuTTY) window.
  10. Click the Close control (upper right corner) in the terminal session (PuTTY) window.
    Click OK in the “PuTTY Exit Confirmation” popup dialog.
  11. Unplug the USB connector from the JACE’s Debug port.

This procedure is simply how to connect using USB serial port for system shell.  More information about functions available once connected can be found in other Knowledge Base articles and in the Jace 8000 Install and Startup Guide

Labels (1)
Labels:
  • TAC IA Series
Attachments
CDM21228_Setup.zip
Tags (1)
  • Find more articles tagged with:
  • RandyDavis20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore