JACE 8000 LED status and accessibility in absence of MicroSD card
  • JACE 8000 LED status and accessibility in absence of MicroSD card
Lt. Commander Reza Lt. Commander
‎2021-03-30 08:40 AM
Last Updated: Crewman ContentModerator ‎2025-09-01 03:34 AM
Both the STAT LED and the BEAT LED is off on the Jace controller and cannot successfully ping the JACE 8000 IP address
TAC IA Series
I/A Series JACE 8000
Warning
Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.
The STAT and BEAT LED remaining in an off state is an indication that no SD card is installed in the JACE card carrier.
When the Micro SD card is installed the STAT LED is solid Green, and BEAT LED is blinking Amber.
Make sure to insert the SD card prior to startup commissioning of the JACE 8000. See JACE-8000 Install and Startup Guide