It appears the BACnet service in a Niagara R2 UNC station stops updating object values after a period of time.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • It appears the BACnet service in a Niagara R2 UNC station stops updating object values after a period of time.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher
  • Kim_Baze
    Kim_Baze

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1397 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

It appears the BACnet service in a Niagara R2 UNC station stops updating object values after a period of time.

Picard Product_Support
‎2018-09-07 03:02 AM

Issue

TAC has discovered an anomaly where R2 BACnet networks operating with the BACnet jar version 523b or earlier may stop updating object values after a period of time, typically over a 24 hour period. In certain large BACnet networks, the polling mechanism in the BACnet service can get into a "deadlock" condition, causing polling to cease. The only way presently to recover from this condition, with version 523b, is to restart the Universal Network Controller (UNC).

Environment

I/A Series R2 (Niagara) station with the BACnet service, version 523b or earlier

Cause

Operating with the BACnet jar version 523b or earlier may stop updating object values after a period of time.

Resolution

Refer to TPA-RKFD-08-0010.00, "Issues with I/A Series R2 BACnet Integrations" for Solution and Action.

BACnet jar 527i (along with the revised bacnet.properties file) was recently released to help prevent the "deadlock" condition from occurring, thus ensuring consistent polling and updating.

In addition, the new jar allows for composite math precision limitation in rewrite determination. Composite math results in values being sent to BACnet controllers from the UNC being slightly different than those being written to and read from the controller itself. For example, if the UNC writes "50.0," the controller will be "49.99999." Since these two values are not the same, the UNC will attempt to re-send the value. With the implementation of the "MinimumFloatDifference" property in the bacnet.properties file, this difference will now be ignored. In past releases, this has caused extra writes, and more importantly, unnecessarily increased the amount of traffic on the network, resulting on slower polling of other BACnet objects.

Our recommendation is to upgrade any UNC with BACnet integrations to the 527i BACnet jar. The files are contained in a .ZIP file - bacnet-2.305.527i.zip. The .ZIP file contains the jar files, the bacnet.properties file, and a READ_ME_FIRST file that has detailed instructions for installing the files.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3288
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of