Issue with multiple valid access attempts at door.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Issue with multiple valid access attempts at door.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1341 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Issue with multiple valid access attempts at door.

Picard Product_Support
‎2018-09-06 01:30 PM

Issue

Swiping valid card immediately following a valid access at the door resets the door's strike time.

Environment

  • CyberStation
  • ACX5740
  • ACX5720
  • CX9680
  • CX9900
  • ACX781

Cause

PE programming needed to override built in behavior

Resolution

Continuum access controllers unlock a door for DoorStrikeTime seconds on valid access and then wait for the DoorSwitch (door contact) to report the door has been opened. Between the door unlock and the detection of door open, the controller will not process a new card swipe, but will buffer up to ONE card swipe transaction for processing at a later time. The buffered card swipe will be processed either when the door strike time expires or once the door is detected open.

 When the controller detects the door open, it resets the door strike time to ONE second and immediately processes a buffered card swipe or a newly detected card swipe. If the card swipe is valid, the controller then overrides the one second strike time with the DoorStrikeTime value.

The behavior explained above, allows for scenarios where many card holders file through a door in a quick manner, such as the start/end of a shift. This allows the system to process valid card swipes in a very fast way without requiring that each card holder waits for the door to re-lock after the person in front goes through.

In some door configurations such as a turnstile, the above creates undesired issues with the operation of the turnstile and must be overridden so that no valid access can be processed until the system has relocked the door, after allowing a card holder through. This can be accomplished with a PE program that disables credential access at the door when the door switch reports the door open, and re-enables credential access when the door switch reports the door has closed.

Sample PE code:

If MainEntrance DoorSwitch = Opened then MainEntrance  DisRdrKpAccess = on else DisRdrKpAccess = off

In cases where no door switch is assigned the door stays unlocked for DoorStrikeTime seconds and if a valid credential access is processed during this time the door strike will be reset to DoorStrikeTime seconds.

In certain scenarios this behavior is undesirable and can be overridden using a PE program so that no valid access is allowed until the door relocks after a previous valid access transaction

 

SamplePEprogram

 

Line EnableAccess

  Door1 DisRdrKpAccess = False

  If Door1 ValidAccess then Goto DisableAccess

 

Line DisableAccess

  Door1 DisRdrKpAccess = True

  If TS > Door1 DoorStrikeTime then Goto EnableAccess

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5777
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore