Is there an object that can be use to allow nciState LON network variable bit values to be entered from the I/A Series R2 graphics?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Is there an object that can be use to allow nciState LON network variable bit values to be entered from the I/A Series R2 gra...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1568 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Is there an object that can be use to allow nciState LON network variable bit values to be entered from the I/A Series R2 graphics?

Picard Product_Support
‎2018-09-10 05:05 AM

Issue

Using a nciState Lon network variable to set operational modes of a MNL-800 application.   Needs to be able to allow these inputs to be set from the GUI.

Environment

MNL-800 application program

Graphical User interface built with the I/A Series (Niagara) R2 system.

Cause

Desire to allow a user at the graphical head end of the BMS system to configure the individual bits of a LON state type network variable.

Resolution

The following discussion is based on the user interface engineering work being done within the WorkPlace Pro engineering tool of the I/A Series R2 system.

The "DynamicCmd" control object found in the "conversion" folder of the Lonworks jar file can be linked to a SNVT_State type Lonworks network variable. 

After linking the DynamicCmd control object to the desired controller shadow object nci type network variable, the DynamicCmd object learns the configuration information for the linked network variable.  The next step in configuring this object for this type of use is to set a name for each control bit element of the network variable.  These defined names are displayed when the GUI user clicks on the control point.  The user then selects the bit field name (from the displayed list) to command and then selects the binary value (True or False)to be written to that bit field.

The following is an example of this control logic where the dynamic device is the MNL-800 controller with the network variable nci_cmd as the input constant and nvo_stat as an output state variable that allows the display of 16 internal bit state variables.

This image shows the configured list of boolean bits that will be configurable via this DynamicCmd_1 object:

When the GUI user selects this command object, the following field list is displayed:

And after selecting the "Fan2-S/S" enable selection, the following popup window is displayed allowing the user to specify the boolean state for that command bit.  The value will be written to the controller when the [OK] button is clicked.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6831
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore