Is there an available program for use with an I/A Series R2 station to calculate sunrise and sunset?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Is there an available program for use with an I/A Series R2 station to calculate sunrise and sunset?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1280 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Is there an available program for use with an I/A Series R2 station to calculate sunrise and sunset?

Picard Product_Support
‎2018-09-10 07:16 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:50 AM

Issue

Customer wants UNC to calculate times to turn outdoor lights on and off.

Environment

I/A Series (Niagara) R2 (any version)

Cause

Customer request for Scheduling functions based on SunRise and / or SunSet.

Resolution

There is a program called "SunClock" that be used for that purpose.

Here is a brief overview of using program modules, if you are not familiar with their use.

  1. Create a folder, such as MyProgLib, for holding your program modules under the Niagara release folder:
  2. Extract the SunClock.sns file from the attached zip file and place it in the folder you created.
  3. Open WorkPlace Pro and open the UNC station into which the program module is to be placed.
  4. Open the Local Library and navigate to the folder you created in step 1 above.
  5. Copy the SunClock.sns module.
  6. Paste the module into the desired container within the UNC station.


The SunClock program module has the following outputs:
sLights        BooleanStatusType     Status Output On between LtsOn and LtsOff times    
pLtsOn         BooleanPriorityType   Priority Output to turn lights on
pLtsOff        BooleanPriorityType   Priority Output to turn lights off
SunRiseTime    DateTimeType          Calculated Sunrise Time
SunSetTime     DateTimeType          Calculated Sunset Time
LtsOn          DateTimeType          Calculated Lights On Time
LtsOff         DateTimeType          Calculated Lights Off Time


The program uses the following properties to control its operation:

LtsOnPriority          Priority level for turning lights on
LtsOffPriority         Priority level for turning lights off
Latitude               Geographic Latitude of location
Longitude              Geographic Longitude of location
SunRiseOffset          Minutes before sunrise to turn lights off
SunSetOffset           Minutes after sunset to turn lights on
DSTEnable              Enable Daylight Savings Time calculation
DSTBeginWeekOfMonth    Week of month that DST starts, 1=first
DSTBeginDayOfWeek      Day of week that DST starts
DSTBeginMonth          Month of year that DST starts      
DSTEndWeekOfMonth      Week of month that DST ends, 5=last
DSTEndDayOfWeek        Day of week that DST ends
DSTEndMonth            Month of year that DST ends


Notes: 

  • Enter Latitude as a positive number for locations in northern hemisphere
  • Enter Longitude as positive number for locations west of prime meridian 
  • Enter negative offsets to set control times after sunrise / before sunset    
     
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6521
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore