Is there an I/A Series G3 Modbus object that converts a PM820 three register date and time format value?
  • Is there an I/A Series G3 Modbus object that converts a PM820 three register date and time format value?
  • WaynePeters
    WaynePeters
‎2018-09-06 11:55 AM
I/A Series G3 - all versions
The Schneider Electric (Square D) PM820 Power Meter provides date and time in a 3 register (6 byte) compressed format. The three registers provide a single timestamp consisting of month, day, year, hour, minute, second.  For example, if the date was 01/25/00 at 11:06:59, the Hex values would be 0119, 640B, 063B.
Hexadecimal High Byte  Low Byte
0119 01 = month 19 = day
640B 64 = year  0B = hour
063B 06 = minute 3B = seconds
Note: Date format is a 3 register (6 byte) compressed format.  Year 2001 is represented as 101 for the year value.
Program object PM_ConvertDateTime.bog decodes and converts the register values to date and time.  The object will split the bytes and decode to individual outputs as well as provide a dateTime output.  Connect the three sequential registers to in, in1, and in2.
Download object: PM_ConvertDateTime.bog
  • TAC IA Series
PM_ConvertDateTime.zip
  • 10978
100% helpful (1/1)