Is there a way to dynamically adjust the "Earliest Start Time" and "Earliest Stop Time" parameter of the I/A Series G3 Optimized Start Stop object?
  • Is there a way to dynamically adjust the "Earliest Start Time" and "Earliest Stop Time" parameter of the I/A Series G3 Optimi...
  • WaynePeters
    WaynePeters
‎2018-09-10 08:31 PM
Is there a way to dynamically adjust the “Earliest Start Time” and "Earliest Stop Time" parameter of the I/A Series G3 Optimized Start Stop object?
I/A Series G3
The I/A Series G3 Optimized Start Stop object “Earliest Start Time” and "Earliest Stop Time" parameters are accessible via the property sheet view.  A program object is required to allow dynamic interface by the user.
Download the ProgramChangeTime program object and save to a known location on the computer.
Copy the ProgramChangeTime object into the station database.
Expose the "Earliest Start Time" and "Earliest Stop Time" by pinning the slots to the Optimum Start Stop object.  Right click on the Optimum Start Stop object and select Pin Slots.
Select "Pin" the Earliest Start Time and Earliest Stop Time and Select OK to expose the slots of the object.
Link the time output of the ProgramChangeTime object to the Earliest Start Time or Earliest Stop Time input as required.
The Actions (changeTime) of the ProgramChangeTime object allows the user to present a dialog box to dynamically enter a new time.
  • TAC IA Series
ProgramChangeTime.zip
  • 7749