Is there a way to determine the total number of BACnet points in an I/A Series G3 station?
  • Is there a way to determine the total number of BACnet points in an I/A Series G3 station?
  • sesa116868
    sesa116868
‎2018-09-06 03:15 PM
I/A Series G3 Enterprise Network Server or ENC station
Engineer wants to know how many BACnet points are used in the I/A Series G3 station.
The I/A Series R2 system provided a way of observing the number of points in the station.  Similar BACnet Driver status screen does not exist in the I/A Series G3 station.
Use the Spy Remote function of WorkBench to look at the number of BACnet device objects and number of BACnet point objects that are in the current station database.
The following is the step by step procedure to display these counts.
  1. Open WorkBench and connect to the Platform.
  2. Log into the Station.
  3. Navigate through the Nav tree to Drivers, expanding that section of the tree.
  4. Right-click on the "BacnetNetwork" and select "Spy Remote" from the Views menu.
The displayed "License Limits" table shows the number of defined objects (Used) and the licensed limit (Limit) for each of those object types.
  • TAC IA Series