Is there a way in Niagara R2 to run a report which lists the BACnet objects instance numbers used in an UNC-520?
  • Is there a way in Niagara R2 to run a report which lists the BACnet objects instance numbers used in an UNC-520?
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 01:02 PM
More BACnet objects are being added to a UNC-520. Is there a way in Niagara R2 to run a report that lists the BACnet objects’ instance numbers used in an UNC-520?
Niagara R2 all versions, UNC-520, UNC-410
NA
Niagara does not offer a report which lists the Instance numbers already assigned in an UNC. About the only way to determine BACnet instance numbers in the UNC is to do a search of the station’s XML file using "instanceNumber" as the search criteria.
  • TAC IA Series
  • 6664