Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Is there a process to downgrade an ENC-410 or ENC-520?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Is there a process to downgrade an ENC-410 or ENC-520?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1566 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Is there a process to downgrade an ENC-410 or ENC-520?

Picard Product_Support
‎2018-09-06 01:27 PM

Issue

Attempting to downgrade the ENC-410 or ENC-520 using the Commissioning Wizard can corrupt the ENC file system making the ENC become unusable.

Environment

I/A Series G3, ENC-410, ENC-520

Cause

Attempting to downgrade the ENC-410 or ENC-520 using the Commissioning Wizard can corrupt the ENC file system making the ENC become unusable.

Resolution

Downgrading from one software release to an earlier release can present compatibility problems. This applies particularly to QNX-based ENCs, as binaries for the (QNX) OS are included in dist files.  However, at times it may be necessary to install an older release onto a ENC, or to restore a ENC to a known good state. To downgrade a ENC, or otherwise “wipe it clean to start over,” a clean distribution file must first be installed.  The following procedure is also detailed in the Niagara AX Platform Guide included with the G3 software.

Installing a clean dist will wipe the file system and install an appropriate version of Niagara platform daemon, resetting the unit to a “near factory state.” Only the following settings are preserved:

• TCP/IP settings
• license files
• brand.properties

All other data is removed from the file system, including station bog files, Px files, modules, etc. In addition, a clean dist restores the factory-default platform credentials and port (3011).  Therefore before installing a clean dist file, make sure to backup station files plus any other modules on the ENC you wish to keep.

Remember, that a “Station Backup” creates a dist file that (when restored) includes the same level of software installed at backup time, so instead of (or in addition to) this type of backup, you may wish to use the Station Copier.

Note that after installing a clean dist, you must recommission the ENC, using the Commissioning Wizard.

---

To downgrade a QNX-based ENC from any G3 3.x build to an earlier release:

Step 1: Before installing a clean dist file, make sure you have backed up the station files plus any other data and modules on the ENC you wish to keep.

Step 2: Start G3 3.x Workbench and open a platform connection to the ENC.

Step 3: Open the Distribution File Installer and click Cleaning button for the !/cleanDist directory.

Step 4: Select the appropriate clean dist file for the platform and install.  The file system clean will take a few minutes, then the ENC will automatically reboot. Wait for the reboot to complete.

Note: After reboot from a clean dist install, the ENC is using default platform credentials and port (3011).

Step 5: Re-install the software versions to the ENC. Use a version of Workbench that runs the same software versions that you want on the UNC, and use the platform Commissioning Wizard to install the desired software build. For details, refer to the section “About the Commissioning Wizard” in the JACE NiagaraAX Install and Startup Guide.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5876
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore