Is it possible to use DC voltage to power the 7793, 7798, and the DPUs (7910, 7920)?
  • Is it possible to use DC voltage to power the 7793, 7798, and the DPUs (7910, 7920)?
‎2018-09-07 01:09 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:49 AM
  • 7793
  • 7798
  • 7910 DPU
  • 7920 DPU
  • DC power
Although this is not the preferred method of powering these devices they are capable of this configuration. We strongly recommend the use of DC voltage be reserved for emergency backup power.
The 7798B Controller, 7910, and 7920 DPUs can be powered by +24 VDC. The DC voltage should be at least +24 VDC - +27 VDC is best.
Refer to the following TCONs for specific wiring detail and installation instructions:
  • 7798B TCON 138
  • 7910 TCON 116
  • 7920 TCON 117