Is it possible to speed up the refresh rate of values in a TGML graphic?
  • Is it possible to speed up the refresh rate of values in a TGML graphic?
  • sesa177673
    sesa177673
‎2018-09-06 12:12 PM
Vista 5.1.X
A customer requires the values to be updated as often as possible.
There is no setting to change the refresh rate in TGML but there are a number of things that can be done to create an efficient graphic.
In Vista 5.1.7 and newer:
  1. On the view menu, there is an item called 'Statistics'. When testing the graphic it possible to see how efficient the graphic is. Items such as a script on document load are very costly, for example.
  2. There is a new property for binding called 'DynamicUpdates'. This can be used to activate a binding later instead of when the graphic is loaded. This can be useful if not all object are visible when the graphic is loaded.
  3. Use scripts only when absolutely necessary.
  • 8200