Is it possible to sort the Vista Workstation alarms only by date, not by group?
  • Is it possible to sort the Vista Workstation alarms only by date, not by group?
  • Sampath_Konda
    Sampath_Konda
‎2018-09-06 03:55 PM
Is it possible to sort the Vista Workstation alarms only by date, not by group in alarm viewer?
TAC Vista 5.x.x Workstation alarms
When you sort the Vista Workstation alarms in the alarm viewer by date, No matter how you sort them they are arranged by date and type OR by groups (Unacknowledged, Acknowledged and then Acknowledged Reset..etc).
See the below picture for example;
No, It is not possible to sort the active alarms just only by the date in Vista Workstation alarm viewer. This will sort by groups.
  • 7500