Is it possible to link to webstation from another website/web portal without needing to log in?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Is it possible to link to webstation from another website/web portal without needing to log in?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa177673
    sesa177673

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1627 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Is it possible to link to webstation from another website/web portal without needing to log in?

Picard Product_Support
‎2018-09-10 11:20 PM

Issue

Is it possible to link to webstation from another website/web portal without needing to log in?

Environment

Vista 5.1.X

Vista Webstation 5.1.X

Cause

A customer may wish to integrate a/some webpage/s from TAC Vista webstation into their company's own internal website.

Resolution

There is an option in TAC Vista web settings that enables a user to be redirected to Webstation from an external application, e.g. another website, and then automatically logged in to Webstation.

The requirement for this to be possible is that the external application and Webstation shares a secret key and an Initialization Vector (IV). These are cryptographic terms and as far as the layman (or sysadmin) is concerned these can be considered to be two passwords of approximately 30 characters each.

The key and the IV are both generated through the "TAC Vista Web Settings" application. The key and the IV are two securely randomized and different 128-bit byte arrays which are then encoded as Base64 for usability purposes. The external application should be programmed to read and decode these two Base64 strings and use them as the key and the IV for the AES (Rijndael) encryption algorithm.

The encryption is used to pass a secret string from the sender (external app) to the receiver (Webstation). This secret string contains the date and time
of the current request (in UTC and in ISO 8601 format) followed by a space and then the user name of the account in Webstation. The secret string should
match the following regular expression or else it is not considered valid:  [0-9]{4}-[0-9]{2}-[0-9]{2}T[0-9]{2}:[0-9]{2}:[0-9]{2}\s.*
 
Example of secret string:
 2005-12-31T21:55:30 fido
 

The encrypted string that is passed to Webstation should be Base64 encoded and also UrlEncoded so the string can be passed in the URL. The UrlEncoded string should be passed to Webstation as a query string parameter where the parameter name is PortalLogin.

Ex: " http://webstation/AlarmListPage.aspx?PortalLogin=%2bxQZvkf5PhtNCsxcuE1I54ZgrwUcQHG%2buPPc7Zn9ThQ%3d"


1. STEPS THE SENDING APPLICATION NEEDS TO PERFORM

a. Construct a string according to the format: YYYY-MM-DDThh:mm:ss user.
b. Encrypt the string using the shared key and initialization vector (IV). The encryption algorithm has to be AES (Rijndael) and key size 128-bit.
c. Encode the encrypted string using Base64.
d. URL-Encode the string.
e. Forward the client to an arbitrary Webstation page and append the query string parameter PortalLogin= followed by the string.

2. WEBSTATION CONFIGURATION

a. The following parameters has been added to Web.Config to support Portal Login:

    TAC.WebStation.PortalLogin.Enabled" value="false" />
    TAC.WebStation.PortalLogin.Key" value="" />
    TAC.WebStation.PortalLogin.IV" value="" />
    TAC.WebStation.PortalLogin.TimeSpan" value="60" />
   
The above values are the default values. Key and IV should be generated by Web Settings and not entered manually. TimeSpan is the amount of seconds the time stamp from the sender can differ from the Webstation server's time when it receives the request.

 

 


 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 8089
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore