Invalid card entry error (0x14BD, 5309 dec) on personnel distribution
  • Invalid card entry error (0x14BD, 5309 dec) on personnel distribution
  • AbeMeran
    AbeMeran
‎2018-09-06 12:17 PM
Personnel object fails distribution with 'Invalid card entry' error.
CyberStation
ACX5740
Personnel object created via CSV file.
Something went wrong during the create process.
Opening the personnel object for edit shows right values, it is not obvious what is wrong with the card information.
Edit the personnel object and make a change in one of the attributes that gets distributed to the controller such as expiration date
After the above, personnel object distributes successfully to the controller.
If lots of records have the problem, make a list view and perform the change on all the objects at once.
  • 8060
100% helpful (1/1)