Interpreting a Modbus register with an ASCO Power Technologies controller using Niagara G3
  • Interpreting a Modbus register with an ASCO Power Technologies controller using Niagara G3
‎2018-09-09 11:19 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 03:55 AM
Doing a Niagara G3 integration with a Modbus controller from ASCO Power Technologies.  What type of Niagara object is required to read register 40158?
Click here to view Modbus Register Map
Niagara G3
ENC-520
Cannot identify what type of object is needed.
The number appears to be an enumerated value (1-22) and is a read-only integer.
Use a Numeric Point.