Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Intermittent master / slave calendar and schedule operation between I/A Series R2 Enterprise Server and UNC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Intermittent master / slave calendar and schedule operation between I/A Series R2 Enterprise Server and UNC.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1212 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Intermittent master / slave calendar and schedule operation between I/A Series R2 Enterprise Server and UNC.

Picard Product_Support
‎2018-09-06 10:46 AM

Issue

Intermittent master / slave calendar and schedule operation between I/A Series R2 Enterprise Server and UNC.  Schedules do not appear follow or recalculate during holiday override conditions.

Environment

I/A Series R2, Enterprise Server, UNC

Cause

Master/slave schedule objects were used however the calendar object only links to the local schedule.

Resolution

Proper implementation of Enterprise Server to UNC master/slave calendar and schedule objects.

Schedule:

  • Master schedule objects reside in the Enterprise Server and slave schedule objects reside in UNC controller.
  • Link the masterOut from a Enterprise Server Schedule object to the masterIn input of one or more UNC Schedule objects.  In case of a communications failure between devices, each UNC retains schedule configurations, as this data is persistently stored in all Schedule objects.

Calendar:

  • Master calendar objects reside in the Enterprise Server and slave calendar objects reside in UNC controller.
  • Link the masterOut from a Enterprise Server calendar object to the masterIn input of one or more UNC calendar objects.  In case of a communications failure between devices, each UNC retains calendar configurations, as this data is persistently stored in all calendar objects.

Linking:

  • Linking of calendar to schedule ... link the local calendar's output to the local schedule's holiday override input (e.g. master calendar to master schedule or slave calendar to slave schedule).  The holiday override should not externally link across the network.
  • In addition, a holiday schedule must not be left blank (no events), “assuming” inactive.  Otherwise, an output that is active upon transition to the holiday day will remain active.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 12160
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of