Integrating several MNB-300 controllers to a UNC-510. How can bias resistors be added to this MSTP trunk?
  • Integrating several MNB-300 controllers to a UNC-510. How can bias resistors be added to this MSTP trunk?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-11 01:00 AM
Integrating several MNB-300 controllers to a UNC-510.  Bias resistors are available on the UNC-520 but not the UNC-510.  How can bias resistors be added to this MSTP trunk?
Niagara R2 UNC-510
The UNC-510 was not designed to include built-in bias resistors for a BACnet MSTP trunk.
The MNB-300 has built-in bias resistors that are disabled by default.  Remove the cover and enable them with the jumpers provided.  Keep in mind that no more than two sets of bias resistors are to be enabled for any MSTP trunk.  For more information, see the MicroNet BACnet Wiring, Networking, and Best Practices Guide (F-27360).