Integrating Windows Active Directory user accounts with EcoStruxure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Integrating Windows Active Directory user accounts with EcoStruxure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
23271 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Integrating Windows Active Directory user accounts with EcoStruxure

Picard Product_Support
‎2020-11-04 03:42 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Issue

Setting up, using, and troubleshooting Windows Active Directory with Building Operation Workstation and WebStation.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation WebStation
  • Windows Active Directory
  • Windows Server

Cause

When integrating EcoStruxure with Windows Active Directory, NO user accounts need to be created in EcoStruxure, all that needs to be done is map the EcoStruxure User Account Group(s) with the Windows group(s) that will be used. 

  • You can map Windows Active Directory groups to Building Operation user account groups if Building Operation runs on a network that uses this directory to manage users and user account groups.
  • A Building Operation user account group that includes a Windows account group can also be a member of another Building Operation user account group.
  • Mapping Windows Active Directory account groups to Building Operation user account groups has advantages both for administrators and operators. Administrators can manage the user accounts in the Windows Active Directory, rather than managing the accounts in two places. Any changes are instantly implemented to the mapped Building Operation user account group. Operations only have to remember the Windows login. Once logged in to a Windows user account that is mapped to a Building Operation account, the user is authenticated to access WorkStation without having to log in a second time.

Note:

  • The Building Operation domain used to map the Windows Active Directory user account groups must be a member of the Windows domain where the Active Directory is located.
  • Windows Active Directory account groups can only be mapped on servers that are based upon Microsoft Windows operating system. Automation Servers, cannot map Windows Active Directory groups. For example, the Windows Active Directory user account groups Main Admin and Main User are mapped to the Building Operation user account groups Administrators and External Users. The External Users user account group is a member of the Operator user account group. The Administrators account group, which is a member of the External Users, inherits access to the Operation workspace.
  • The user will then log into Windows on the PC where the WorkStation is installed. When logging into EcoStruxure Workstation the authentication is automatically done from the Windows user account.

Resolution

NOTE: Active Directory association cannot be achieved using the inbuilt Local Domain

  1. Create a new EBO Domain and associate it with your active windows Domain.AD Domain.png
    NOTE:
    It is best to only use the Domain (Netbios) name (as shown above) when adding the Windows Domain name to this property.  Using the full DNS Domain name, for example, eur.gad.schneider-electric.com will cause issues when utilizing other features that require active directory authentication.  One example where this has been identified is with Change Control.  
  2. Create an EBO Domain Group within that new Domain and associate it with the Windows Domain Group in which the Windows Active Directory user(s) reside.Ad Group.png
  3. Log in using Windows Username, Password, and Domain rather than EBO credentials. When logged on to the Enterprise Server PC as a Domain User it is also possible to select the "Log on as" box.

See WebHelp:

  • How to Create and Configure a Domain
  • Conceptual Information on Windows Active Directory User Groups
  • How to Create User Account Groups

Troubleshooting Windows Active Directory with Workstation

  1. Log in Error: Wrong user name or password
    Wrong password.png
  2. If the EcoStruxure Building Operation Domain has the same name as the Windows Active Directory domain name, it will expect the user account to exist locally in the Building Operation domain.
    EBO_Domain.png
  3. Log in Error: "User account not associated with a group. Contact your Administrator."
    Missing Group.png
  4. Verify that the Windows user is a part of the Windows group configured in the Building Operation Group settings. In order to identify every group that the current windows user belongs to, run the command: whoami /groups
    whoami_groups.png
  5. Once the Windows user has been confirmed as a member of the configured Windows group, try changing the Log On as credentials for the Enterprise Server service. The default user that is used when installed is the "Local System account". The Windows account used to run the Enterprise Server service needs "read access" to all places (e.g. OUs) in the Active Directory where user groups potentially involved in an EBO Windows log-on can be found.

    Note: By default, all domain users in an Active Directory have read access to Active Directory "Users and Computers" objects so it is the sites that have restricted this in some way that may face issues. You do not need to use “domain admin” type accounts for this as they are granted way too much authority in general. An account that has read access to sufficient parts of the AD while having only normal local user privileges on the machine where the Enterprise Server is running will suffice.
    1. From the Windows Start menu, launch Computer Management. In Computer Management go to Services and Application > Services.
    2. Find Building Operation X.X Enterprise Server, select it and Stop the service.
      Services.png
    3. Right-click on Building Operation X.X Enterprise Server and go to Properties. Select the Log On tab.
    4. Under Log On as select "This account". Enter a Windows user login that has sufficient Windows rights for the Enterprise Server to log on as.
      Service_Account.png
    5. Click OK and then start the service again.
    6. Log in to Workstation again using Active Directory.

Troubleshooting Windows Active Directory with WebStation

From version 1.5.0 and up, using Windows Domain accounts is supported in WebStation. However, the following must be done in order to log in.

  1. Must use HTTPS.
  2. Must enter your Windows username and password.
  3. Must enter the domain as the Windows domain as defined within Building Operation.  See below:

    AD_DNSDomainName.png

    An example log-on format is shown below when using the above configuration when using WebStation:
    WebStationLoginExample.png  
    Alternatively, if the following is configured in Building Operation:
    AD-WindowsDomain#2.png

    WebStation log-on will look as follows: 
    AD_WebStationLogon.png

Download a TVDA for Single Sign-On Instructions

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (8)
  • Find more articles tagged with:
  • 12985
  • CraigEllis20
  • DavidKendrick19
  • HernanUruena23
  • HernanUruena24
  • JonathanHernandez20
  • RobertAndriolo20
  • RobertAndriolo21
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore