Integrating MNL-VAV controller into the EBO environment

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Integrating MNL-VAV controller into the EBO environment
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3088 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Integrating MNL-VAV controller into the EBO environment

Kim_Baze Schneider Alumni (Retired)
‎2019-01-31 11:46 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:35 AM

Issue

Integrating MNL-VAV controllers into the EBO system successfully

Product Line

EcoStruxure Building Operations, TAC IA Series

Environment

  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • I/A Series MNL VAV

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

  • Lost flow balancing values during integration
  • Lost S-link offset calibrations

Resolution

Use the following steps to bring a controller into the Automation Server with all data intact.

  1. Using WorkStation connected to the AS/AS-P; right click on the LonWorks Network and select New then Device.
  2. Choose the appropriate device object type from the list for the MNL-VAV controller being added, give it a name and click Next.
  3. Type in the Neuron ID or use the Service pin method to identify the controller.
  4. Check the box next to “Commission” and the radio button next to “Keep current configuration in the device” and click “Create” then click “Close” when complete.
  5. Right-click on the new device object in the tree and select MNL and then “Backup flow balance information”. When this is complete notice the blue circle with a white checkmark next to the nciHighFlowCal and nciLowFlowCal SNVT’s indicating the AS-P DB contains the balance data from the controller.
  6. If special S-link offset values exist in the controller right click on the device object in the tree and select MNL and then “Backup S-link offsets”.
  7. Right-click on the controller device object and select MNL and “Assign application” and click on the appropriate application file for this controller and click on “Assign”.
  8. Right-click on the controller and select MNL and “Download application”. Click on “Close” when complete.
  9. Right-click on the controller and select MNL and “Restore the flow balance information”
  10. Right-click on the controller and select MNL the “Restore S-link offsets”.
  11. Verify all data is correct and the controller is functioning properly.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (3)
  • Find more articles tagged with:
  • mnl
  • RandyDavis19
  • vav
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore