Integrating I/NET with a Firefighters Smoke Control Station (FSCS)
  • Integrating I/NET with a Firefighters Smoke Control Station (FSCS)
‎2018-09-06 04:55 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:49 AM
Can an I/NET control system be connected to a Firefighters Smoke Control Station (FSCS)?
Which I/NET product is often recommended as a Fire Alarm Panel (FAP) Interface?
  • I/NET
  • FSCS
  • UL 864
Smoke control in an HVAC application.
I/NET can be connected to a UL 864 listed panel providing contact inputs (for Lamps/Enunciator) and contact outputs delivering override switch status.
Only the 7797-12-U8 is approved for use as the primary means of serial alarm reception in a listed smoke control system.
Refer to TCON 231, Smoke Control Systems Manual, FSCS Interface Options for more details.
  • TAC INET
  • 877