Inputs on PCU are consistently reading too low
  • Inputs on PCU are consistently reading too low
‎2018-09-06 03:27 PM
I/NET
There may be a short on one or more of the inputs or the power supply may have a problem.
To check for a short in the inputs:
  1. Remove all the inputs
  2. Place one input back on the PCU
  3. Check the point value
  4. If it is normal, install and check the next input.
  5. Repeat through all inputs
In summary, a short in a sensor's input to the PCU will affect all inputs on that bank.
  • TAC INET