Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Input scaling issues with the use of 0 to 5 Vdc and 0 (or 4) to 20 Milliamp transducers on a MNB controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Input scaling issues with the use of 0 to 5 Vdc and 0 (or 4) to 20 Milliamp transducers on a MNB controller.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa116868
    sesa116868

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1531 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Input scaling issues with the use of 0 to 5 Vdc and 0 (or 4) to 20 Milliamp transducers on a MNB controller.

Picard Product_Support
‎2018-09-06 02:50 PM

Issue

Input scaling issues with the use of 0 to 5 Vdc and 0 (or 4) to 20 Milliamp transducers on a MNB controller.

Environment

MNB Series Controller application program using Analog Input voltage or current inputs.

Cause

The resolution of the Analog Input object value is determined by the maximum value that can be processed.
If the scaled input range is less than 163.84, the output resolution is 0.01
If the scaled input range is greater than 163.84, the output is an integer value.

Resolution

When programming the Analog Input object in the WorkPlace Tech Tool, it is important to properly configure the input range and scaled value range for this object.

If configured for a 0 to 5 VDC input, the sensor properties must be configured as follows:
Input Sensor Type (Type): 5 - Volts
Input Low Value (LInput): 0
Scaled Low Value (LScale): 0
Input High Value (HInput): 5
Scaled High Value (HScale): (value, up to 16383, corresponding to 5 volt input) See note below.

If configured for a 0 to 20 milliamp or 4 to 20 milliamp input, the sensor properties must be configured as follows:
Input Sensor Type (Type): 4 - Milliamp
Input Low Value (LInput): 0 or 4 (depending on transducer)
Scaled Low Value (LScale): 0 (value corresponding to LInput sensed value)
Input High Value (HInput): 20
Scaled High Value (HScale): (value, up to 16383, corresponding to 20 milliamp input) See note below.

NOTE: The HScale value should be set to give an output value for the Analog Input object that corresponds to the maximum temperature, flow, cfm, etc. that the sensor is measuring. The resolution of the value processed by this object must be taken into account when setting the HScale value because the input to output scaling and precision depends on this scaling constant. If the HScale value is less than 163.83, the input resolution is two decimal places and if greater than 163.83, integer resolution. An example of where this scale range is critical would be the use of a 0 to 5 volt air pressure transducer measuring an air pressure of 0 to 2 InWC. If the HScale is set to 2, the output would only resolve to 0.01. If the HScale value were set to 2000, the output would be in thousandths of an InWC, giving you an effective resolution of 0.001. Since this value is one thousand times the actual measured pressure, this 1000x scale factor would also have to be taken into account in any use of that value within the application.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2948
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of