Input and Output resolution of Xenta controllers
  • Input and Output resolution of Xenta controllers
  • SESA116857
    SESA116857
‎2018-09-06 01:56 PM
What is the A/D resolution of the Inputs and Outputs on the Xenta product line?
Xenta 28x
Xenta 30x
Xenta 4xx I/O Modules
Due to project specifications and requirements it is important to know the input and output resolution of the Xenta product line.
The Xenta Product line has resolutions for inputs and outputs accordingly:
Controller Thermistor Inputs Universal Inputs Analog Outputs
281 12 bit   12 bit
282 12 bit   12 bit
283 10 bit   12 bit
301 12 bit   12 bit
302 12 bit   12 bit
421A/422A   12 bit
451/452 12 bit 12 bit
451A/452A   12 bit 8 bit
471   12 bit
491/492     12 bit