Input/Output limitations in Xenta 700 series controllers.
  • Input/Output limitations in Xenta 700 series controllers.
  • Sacco
    Sacco
‎2018-09-11 03:58 AM
tam32 Error: "Max limit if number of in- and outlets is reached, this application cannot be generated."
Xenta 7xx
Xenta 700 series programmable controller.
Too many inputs and/or outputs in a Menta Object will cause generation to fail.
Reduce the amount of inputs or outputs in the program to < 500 total. This can be accomplished by splitting the faulty program into multiple Menta Objects (programs) in the controller.
Labels (2)