InitCrypkey Error -103 or InitCrypkey Error -102 when running Checklic license utility

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • InitCrypkey Error -103 or InitCrypkey Error -102 when running Checklic license utility
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3220 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

InitCrypkey Error -103 or InitCrypkey Error -102 when running Checklic license utility

Picard Product_Support
‎2018-09-07 03:38 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-10-07 08:40 AM

Issue

Error when running the Checklic license utility:

  • "InitCrypkey Error -103: NETWORK: REPLY FROM NETWORK DRIVER IS BAD"
  • "InitCrypkey Error -102: NETWORK: NETWORK DRIVER APPEARS TO NOT BE SERVING THIS DIRECTORY"

Product Line

Other, TAC Vista

Environment

  • LNS 3.0
  • LNS Turbo Edition (Ver 3.2)
  • LonMaker 3.0
  • LonMaker 3.1
  • LonMaker Turbo (Ver 3.2)
  • Vista

Cause

A problem has occurred with the LonMaker licensing.

Resolution

There are two procedures for fixing this problem. Try Procedure 1 first, and if the license still has the same problem, try Procedure 2.

Internet access may be required for Procedure 2 to in order to download the setupex.exe and cks.exe programs and request a replacement license.

Procedure 1:

  1. Confirm that the Windows Crypkey License service is started. To confirm, click Start > Control Panel > Administrative Tools > Services. Verify the Crypkey License status is Started. Also verify that the startup type is Automatic. If not, right-click the name and then click Start. Double-click the name to enter the properties dialog and change the startup type to Automatic. Close the Service window.  
  2. Confirm the Crypkey NetworkX driver is started by running C:\Program Files\Common Files\Microsoft Shared\MSInfo\Msinfo32.exe. Expand System Summary > Software Environment > System Drivers in the category tree in the left pane, then locate NetworkX in the right pane. Confirm that the State is Running and the Status is OK. Close the System Information window.
    If you cannot find these software components, uninstall the Echelon Software product, reboot, and reinstall the product. Antivirus and Internet security software can interfere with the proper installation of the software. Disable such software before you re-install the Echelon software product.
  3. At this point, if you are still unable to run your LonMaker or LNS application because of a License Access error message and if the Checklic license utility still reports a -102 or -103 error, follow the steps in Procedure 2.

Procedure 2:

  1. Check to see if two files exist in the C:\Windows\LNS Licenses folder.
    • setupex.exe
    • cks.exe
  2. The LNS Licenses folder is hidden; if you do not see it, open the Windows Explorer Tools menu, click Folder Options, and in the View tab, select Show Hidden Files and Folders and clear Hide Protected Operating System Files (Recommended). If you don't see these files, download them from Echelon and extract them to the C:\Windows\LNS Licenses folder.
  3. Open a Windows command prompt by clicking Start > Run and typing in cmd (or command for Windows 98).
  4. Type the following command to change your working directory: cd "\Windows\LNS Licenses"
  5. Type the following command: setupex /U
  6. Reboot the computer.
  7. Repeat steps 3 and 4, and then type the following command: setupex
  8. Reboot the computer.
  9. Open a Windows command prompt and enter "checklic lonmaker.vsl" for the LonMaker Tool or "checklic nsseng.exe" for other LNS tools and applications.
  10. If no errors appear, then the LNS application should start. Exit now.
  11. If the GetAuthorization Error -4/GetAuthorization Error -1 error is shown, which is expected, try opening/creating network. If the -4/-1 error remains, use the license wizard to request replacement credits.
  12. If the InitCrypkey Error -102/-103 error is shown, delete the following files under C:\Windows\LNS Licenses (do not delete other files from the LNS Licenses folder):
    • For the LonMaker tool:
      • LonMaker.rst
      • LonMaker.ent
      • LonMaker.key
      • LonMaker.41s
    • For an LNS tool or application other than the LonMaker tool:
      • nsseng.rst
      • nsseng.ent
      • nsseng.key
      • nsseng.41s
  13. Delete esnecil.ind in the C:\windows\system32 folder.
  14. Reboot the computer.
  15. Run the Checklic license utility again.
  16. If the GetAuthorization Error -4/GetAuthorization Error -1 error is shown, which is expected, try opening or creating a network. If the -4/-1 error remains, use the license wizard to request replacement credits.
  17. Once the license is fixed, download and install the LNS Licensing Update 2006.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4102
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore