InfinityProgram/BACnet program, property inconsistencies when viewed from Infinity vs BACnet side
  • InfinityProgram/BACnet program, property inconsistencies when viewed from Infinity vs BACnet side
  • AbeMeran
    AbeMeran
‎2018-09-10 11:18 PM
PE Programin bCX/b3 seens as disabled/idle in list view even though program is running and operating normally.
AS
In the screen shot above the program is reported as ACTIVE and ENABLED from a Continuum perspective (List View on the Infinity side) BUT idle and disabled from a BACnet perspective. (List view on BACnet side)
Printing the programs BACnet properties from the command line shows that the program is actually In Service and executing.
CyberStation
bCX
b3
BACnet
Inconsistencies between Andover and BACnet protocol which in some cases have conflicting property values.
When looking at properties of BACnet objects from Cyberstation make sure to be aware of the context in which the properties are being shown (BACnet or Continuum) and ignore non applicable properties.
For example, if looking at the program from BACnet perspective look at the OutOfService property instead of the State property.
  • 12140