InfinityOutput value does not reflect the actual physical value.
  • InfinityOutput value does not reflect the actual physical value.
  • AbeMeran
    AbeMeran
‎2018-09-06 12:47 PM
After setting InfinityOutput to a pulse value the value prints as ON even when the relay is physically OFF
Output print format is set to $### and output is NOT inverted or overridden.
All CXs
All b3s
All i2s
Function as designed
When an output is commanded to a pulse value (i.e. 5) the relay energizes and then de-energize after 5 seconds, the value property retain the last value the output was commanded to, in this case 5.
The display format $### displays values greater than zero as ON, zero values as OFF,  and values less than zero as -ON.
The print format should be set without the '$' to display the pulse value (5)
To make the system show the actual physical value of the output print the OverrideValue instead of the Value.
  • 7148