In a Niagara R2 / Microsmart integration with revision 9 controllers, what's the best way to implement the MsL9Value object?
  • In a Niagara R2 / Microsmart integration with revision 9 controllers, what's the best way to implement the MsL9Value object?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 02:49 PM
Unknown Environment
Unknown Cause
The only way to effectively implement this object is to do the following:
  1. Create a virtual AI point in the revision 9 MicroSmart controller. This is a standard AI point with no input address assigned to the INPUT field.
  2. Learn it into the UNC station.
  3. Create a MsL9Value object in the workspace of the virtual AI point's shadow object.
  4. The only property that needs to be assigned is the "logpt". This must be a numeric value 1 to 250. If more than one MsL9Value object is used under a L9 controller, it should be a different number in each.
Refer to ibsMS-2.302.514a Release Notes.pdf for additional details of this object.
The UNC can now send a value down to the virtual AI which, in turn, can be used as a manual setpoint input to a Loop point or Mode Control point. The MsL9Value object can be linked to a GxText object providing the building operator the ability to change the value from a web graphic.
  • TAC IA Series
  • 2968