In a Niagara G3 Modbus integration, a register contains 16-bits which must be split into two 8-bit values (a high byte and a low byte).
  • In a Niagara G3 Modbus integration, a register contains 16-bits which must be split into two 8-bit values (a high byte and a ...
‎2018-09-10 12:55 AM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM
There are no existing objects in Niagara G3 that can split a 16-bit Modbus register into two 8-bit values with one representing the high byte (bits 8-15) and another the low byte (bits 0-7).
Niagara G3 all versions
Modbus integration of a 3rd-party product using 16-bit values which must be split into two 8-bit values.
A program object is available below that will achieve this requirement.  The output of this object generates two 8-bit integer values and two string values for use with logic programming and display purposes.
Text file of program code
  • TAC IA Series
RegisterToBytes.zip
  • 5510