A GCM has been removed in the field and replaced with a newer product (i.e. a Niagara Jace or a SmartStruxure AS).  How can the GCM be disabled from communicating in TreeTech without actually deleting it?
TreeTech (all revisions)
The GCM's programming logic will be used for a short period of time as a reference.  Then, the entire GCM will be deleted from TreeTech.
Right-click on the GCM and go to Properties.
Click the Offline Status tab.
Select Offline from the drop-down menu.
Close the window.
Offline mode disconnects the GCM database in TreeTech from the field.
  • TAC IA Series