Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

In Niagara R2 or G3, the AX Lon Tunnel service fails to start.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • In Niagara R2 or G3, the AX Lon Tunnel service fails to start.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1772 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

In Niagara R2 or G3, the AX Lon Tunnel service fails to start.

Picard Product_Support
‎2018-09-11 06:59 AM

Issue

After installing the Niagara AX Lon Tunnel Client, the service fails to start and Windows displays the following error:

Could not start the NiagaraAX Serial Tunnel service on Local Computer.
Error 1068: The dependency service or group failed to start.

Environment

I/A Series AX Lon Tunnel Client

Cause

There are two possible causes of this issue.

  • The LON port specified is already in use and assigned to a physical LON adapter.  The LON adapter assigned to this port may not necessarily be currently installed into the computer.
  • One of the underlying Windows functions or services required by the AX Lon Tunnel is not installed or is corrupted.

Resolution

To verify that the LON port you have selected is not already installed in the computer, perform the following steps:

  1. Open the "LonWorks Interfaces" applet from the Windows Control Panel (Procedure describes operation with OpenLDV 4.00 installed.  The procedure for OpenLDV 3.20 or OpenLDV 3.40 is similar to what is shown in the following steps.
  2. Under the "View" menu, insure that "Show detached interfaces" is checked.
  3. Select a LON port that is not already shown in the list and enter it in the "Lon Port" field of the "Niagara AX Lon Tunneling" Windows control panel applet.

If the LON port name is valid and the NiagaraAX Lon Tunnel service still displays the 1068 error message, an issue could be occurring with another Windows service or DLL file.  Microsoft provides a method of diagnosing and possibly correcting this type of issue.

  1. Open the Windows Start Menu and in the "Search Programs and files" box enter the command:
          cmd
  2. In the Command Prompt window, type in the following command:
          sfc /SCANNOW
    This command "scans integrity of all protected system files and repairs files with problems when possible".
    In the event that this process finds an uncorrectable issue, the program will stop, displaying an appropriate diagnostic message.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 15703
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of