In Niagara R2 Workplace Pro, a Save Runtime DB command on a UNC does not work. This error message appears: "DB ADMIN COMMAND ERROR EXCEPTION; CONNECTION REFUSED".
  • In Niagara R2 Workplace Pro, a Save Runtime DB command on a UNC does not work. This error message appears: "DB ADMIN COMMAND ...
  • sesa119747
    sesa119747
  • sesa116871
    sesa116871
‎2018-09-06 02:55 PM
  • Niagara R2 Workplace Pro
  • UNC
The UNC has its http port configured for a port number other than the default port of 80. A line must be added to the station.properties file to specify the new port number.
  1. Open the admin tool and log into the UNC (not the station database).
  2. Right-click on the station name that indicates "running" and select Edit > Properties. The station.properties window will open (typically indicates autoStart=true and autoRestart=true).
  3. Add a line to this file that specifies the new port number.  For example, if the station database was configured to use port 8080, the line would read:  httpPort=8080
  4. Choose File - Close and Save when prompted.
NOTE: To enable this change, the UNC must be rebooted.