In Niagara G3, the SNMP driver reference manual refers to three MIB files required so that the SNMP Point Manager can "discover" and "add" SNMP points as needed.  The filenames are:
TridiumR3-MIB.my
RFC1155-SMI.mib
RFC1213-MIB.mib
Where can they be found?
Niagara G3
The three files are not easily located.
The TridiumR3-MIB.my file is installed with the version of Niagara G3 installed on the host computer.
The other two files (RFC1155-SMI.mib & RFC1213-MIB.mib) can be found on the World Wide Web by searching using their specific filenames.