In Niagara G3, how can the status (up / down) of a device object be trended?
  • In Niagara G3, how can the status (up / down) of a device object be trended?
  • sesa116871
    sesa116871
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 02:27 PM
Niagara G3
Recording a connected controller's communication status
Within the Wire Sheet that contains the device shadow object:
  1. Insert a StatusDemux object (from the kitControl pallet, Util folder).  Link the "Status" from the device object to the "In Status" of the StatusDemux object
  2. Insert a Boolean Writable object.  Link the "Down" slot of the StatusDemux object to the "In10" of the Boolean Writable object
  3. Add a BooleanCov history extension to the Boolean Writable object.  This will then track the up / down status of the device.
  • TAC IA Series
  • 3927