In Niagara G3, how can an objects value be displayed in a graphic and not its status?
  • In Niagara G3, how can an objects value be displayed in a graphic and not its status?
  • sesa116871
    sesa116871
‎2018-09-06 02:26 PM
Niagara G3
Default BoundLabel properties of the object are set to display the value and status. It must be adjusted to display only the value.
In the BoundLabel properties of the object, the default text format is
This displays the value and the status of the object. To display just the object's value, edit the format to
%out.value%
The object will then display only the present value in the graphic.
  • TAC IA Series
  • 3962