In Niagara G3, how can a button on a graphic be created that will open a Schedule Editor?
  • In Niagara G3, how can a button on a graphic be created that will open a Schedule Editor?
  • sesa119747
    sesa119747
  • sesa116871
    sesa116871
‎2018-09-06 02:33 PM
  • Niagara G3
  • kitPx palette
  • Schedule Editor
To open Schedule Editor with a click of a button, create a hyperlink button in the graphic and link to the schedule object.
Perform the following steps:
  1. In the kitPx palette, drag a hyperlink button into the graphic
  2. In the Properties of the hyperlink button, click the "..." button to the right of the "hyperlink" field. The hyperlink window appears.
  3. In the hyperlink window, click the down arrow next to the open folder icon, and select Component Chooser. In the select Ord window, navigate to the desired schedule object. Click on the object, then click OK
  4. In the hyperlink window, click on the (Default View). The list will expand. Click on Scheduler.
  5. In the hyperlink window, click OK
  6. In the Properties window, click OK
  7. In Runtime mode, click on the newly created button. The Schedule Editor will now appear.
  • TAC IA Series
  • 3662