In Niagara G3, how can a Boolean object's "False" condition be made to disappear?
  • In Niagara G3, how can a Boolean object's "False" condition be made to disappear?
  • sesa116871
    sesa116871
‎2018-09-06 02:26 PM
  • Niagara G3
  • Boolean Object
BoundLabel properties must be adjusted for the desired operation.
  1. In the BoundLabel properties of the object, right-click on the "visible" field, and choose "Animate"
  2. In the Animate window, click on the drop-down for the "Converter Type", and choose "I Boolean to Simple"
  3. Click the drop-down for the "False Value", and select "false"
  4. Click OK to close the Animate window
  5. Click OK to close the BoundLabel properties window
  6. Save the graphic
Now, when the object has a value of "false," it will not be visible in the graphic.
  • TAC IA Series
  • 3963