In Niagara G3, how can a BACnet Read Only proxy point be changed to a Writable Proxy Point?
  • In Niagara G3, how can a BACnet Read Only proxy point be changed to a Writable Proxy Point?
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 01:12 PM
In Niagara G3, a BACnet proxy point was initially added to the database as Read only; how can it be change to a BACnet Writable proxy point?
Niagara G3 all versions
BACnet proxy point type (read only. writable, etc.) is selected when the proxy point is first added to the database. The BACnet Proxy Point was initially discovered and added to the database as Read Only Proxy Point.
Unfortunately, once the BACnet Proxy Point is added to the database its Type value can not be changed. The Proxy Point will have to be deleted, rediscovered and re-added to the database. This time when adding the Proxy Point to the database, make sure to select writable for Type.
  • TAC IA Series