In I/A Series G3, is there an object that provides a BooleanStatus output reflecting the overridden status of a Boolean Writable or Numeric Writable?
  • In I/A Series G3, is there an object that provides a BooleanStatus output reflecting the overridden status of a Boolean Writa...
  • WaynePeters
    WaynePeters
‎2018-09-10 11:19 PM
I/A Series G3
Need to detect and / or act upon the status conditions of a Boolean Writable or Numeric Writable object.
A StatusDemux object can be linked to the Boolean Writable or Numeric Writable object to provide a Boolean output for each of the status flags (Alarm, Down, Fault, Null Status, Disabled, Overridden, Unacked Alarm, and Stale).
Within the Wire Sheet that contains the Boolean Writable or Numeric Writable object:
  • Insert a StatusDemux object (from the kitControl pallet, Util folder).
  • Link the "Out" from the Boolean Writable or Numeric Writable object to the StatusDemux "In Boolean" or "In Numeric" input.
  • TAC IA Series
  • 12205