Implementing/Troubleshooting Periodic Reports in Vista Workstation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Implementing/Troubleshooting Periodic Reports in Vista Workstation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1171 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Implementing/Troubleshooting Periodic Reports in Vista Workstation

Picard Product_Support
‎2018-09-07 04:04 AM

Issue

How to set up a periodic report in Vista Workstation.  Troubleshooting techniques to solve a periodic report that will not run.

Environment

Vista Workstation 5

Cause

There are three objects required to work together.  They are:

  • Time Event - Object
  • Report
  • Report - Periodical

Resolution

Verify settings in each of the three Vista objects

Time Event - Object

  1. Create a Time Event - Object.  Right-click and go to Properties.
  2. View the Time Event Settings Tab
    1. Choose the interval type and frequency.
    2. Ensure a start time is checked and occurs prior to when the report should run.
    3. Check a stop time.  If a stop time is needed, leave it checked.  If not, uncheck it.
  3. Click OK
  4. Right-click again and go to Properties.
  5. View the General Tab
    1. Description is optional
    2. Next Event: should be populated with a date and time.

Report

  1. Create a Report object.  Right-click and go to Properties.
  2. Go to the Report Tab
    1. If the report is to be printed, define a printer.
    2. If the report is to be saved to the hard drive, define a destination folder.
    3. Define a report file name.  This will be the name of the saved folder.
    4. If multiple copies are to be saved, uncheck overwrite existing file.  Files will be saved with a datetime extension on the file name.
  3. To insert a trend log or value into the report, navigate to the report in Vista Workstation, right click, and go to edit. Select a cell in excel towards the top left of the page where the trend or value will be inserted. In excel menus, navigate to Vista Links > Insert > Trend Log or Value. Browse in the value or trend log out of the vista database, adjust settings to the project preference and click okay. Finally make sure that the report is saved to the Vista database by navigating to Vista Reports > Save.

 

Report - Periodical

  1. Create a Report - Periodical.  Right-click and go to Properties.  This is the object that will tie together the Time Event - Object with the Report.
  2. General
    1. Report:  Browse to the Report object in the Vista database
  3. Settings
    1. Active: must be checked.
    2. If the report is to be printed, check Print report.
    3. If the report is to be saved to the hard drive, check Save copy
  4. Event Settings
    1. Event:  Browse to the Time Event - Object in the Vista database
    2. If the report is to run when the event begins, check Tripped
    3. If the report is to run when the event ends, check Reset.  At least one of these should be checked.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4208
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore