Issue
If the HOA switch on my 7716 is NOT in the automatic position, can the software alert the host that this point is in manual override?
Environment
I/NET site with 7716 controllers, or other controller which have the HOA switch. HOA is short for Hand-Off-Auto
Cause
If the HOA switch on my 7716 is NOT in the automatic position, can the software alert the host that this point is in manual override?
Resolution
Yes, but the point(s) must be set up.
Example for 0000 DO HOA:
Address: 0008
Type: DI/DA
Class: Ext
Point Name: HOA for 0000 DO
Set Number of Bits = 2
Set State Description = AUTO, where State Descriptions are 1 Auto, 2 ON,
3 OFF
For DA point, set Normal = Auto
For more information, please refer to TCON096