If the HOA switch on my 7716 is NOT in the automatic position, can the software alert the host that this point is in manual override?
  • If the HOA switch on my 7716 is NOT in the automatic position, can the software alert the host that this point is in manual o...
‎2018-09-07 12:32 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:48 AM
I/NET site with 7716 controllers, or other controller which have the HOA switch. HOA is short for Hand-Off-Auto
Yes, but the point(s) must be set up.
Example for 0000 DO HOA:
Address: 0008
Type: DI/DA
Class: Ext
Point Name: HOA for 0000 DO
Set Number of Bits = 2
Set State Description = AUTO, where State Descriptions are 1 Auto, 2 ON,
3 OFF
For DA point, set Normal = Auto
For more information, please refer to TCON096
  • TAC INET