If power is removed from a UNC, how long before the UNC shuts down?
  • If power is removed from a UNC, how long before the UNC shuts down?
  • Kim_Baze
    Kim_Baze
‎2018-09-06 02:54 PM
UNC
A UNC will not immediately shut down after power is removed.
By default, the number of seconds to elapse after detecting an AC power failure and beginning the shutdown of the UNC or ENC is 60 seconds. This can be adjusted by opening the drivers.properties file and changing the value referenced in the power.shutDownDelay entry.
For more information refer to the NiagaraSysmonEngNotes.pdf
  • TAC IA Series
  • 2788