Identify Automation Server IP address to retrieve the password reset Session ID

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Identify Automation Server IP address to retrieve the password reset Session ID
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
659 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Identify Automation Server IP address to retrieve the password reset Session ID

Sisko GavinHe Sisko
‎2025-09-22 03:59 PM

on ‎2025-09-22 03:59 PM

Issue

How can the IP address of a Standalone Automation Server be determined so that the password reset session ID can be retrieved?

Product Line

EcoStruxure Building Operation

Environment

Automation Server

Cause

Due to the lack of available information regarding the Standalone Automation Server, it is not possible to determine its IP address. Beginning with version 3.2, a password is required to log in via USB in order to obtain the IP address. Consequently, obtaining the session ID is not feasible under these circumstances.

Resolution

To reliably obtain the IP address of the controller, an alternative discovery method should be employed. The most robust and effective approach is to perform network traffic analysis using Wireshark. By monitoring broadcast or ARP packets during the controller's startup or communication phase, the IP address can be identified. 

 

Prerequisites:

  • Access to the device’s physical label to obtain its MAC address.
  • Administrative access to a PC on the same network segment as the device.

Procedure:

  1. Obtain the Device MAC Address:
    • Locate the MAC address on the device’s label (e.g., 00:80:f4:46:d6:d2).GavinHe_0-1758543123718.png
  1. Network Setup:
    • Connect both the device and the PC to the same network segment (broadcast domain).
    • For optimal results and minimal background traffic, connect the device directly.
  2. Start Packet Capture:
    • Launch Wireshark on the PC.
    • Select the appropriate network adapter and begin capturing traffic.
  3. Power Cycle the Device:
    • Reboot or power cycle the device to initiate network communication.
  4. Apply MAC Address Filter:
    • In Wireshark, use a display filter to isolate traffic from the device’s MAC address, e.g. eth.addr == 00:80:f4:46:d6:d2 or eth.addr == 00-80-f4-46-d6-d2 (It is possible to use either colon or dash notation)
  5. Identify the Device IP Address:
    • Observe the captured packets for DHCP, ARP, or other IP-based communications from the device.
    • The source or destination IP address in these packets will reveal the device’s assigned IP.GavinHe_1-1758543123719.png

Next Steps for the EcoStruxure Automation Server:

  • Once the device IP is identified, access the EcoStruxure BMS Server.
  • Set the server to Password Reset Mode.
  • After resetting the password, Copy the Session ID  as required.

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • GavinHeward25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore